Technical Section WAGO

| Kategorie: Leták / Datasheet Firemní tiskovina  | Tento dokument chci!

Vydal: WAGO Elektro spol. s r.o.

Strana 28 z 44

Jak získat tento dokument?






Poznámky redaktora
3) 470 10 (5. permissible tem- perature rise: 50°C (122°F) Table 5 Conductor Size Copper Test Duration Test Current AWG mm² A 14 (2.wago.3) 750 8 (8.6) 3900 1 (42. permissible tem- perature rise: 30°C (86°F) Max. Static Heating Test: Test current: Terminal block rated current Test current: Increased test current (see Table 6) Test duration: days Test duration: days Max.4) 4900 1/0 (53.5) 5050 2/0 (67.1) 300 12 (3.4) 6400 3/0 (85.27 www. In the following example, AWG (35 mm²) ground conductor termi- nal block (285-635) tested for seconds 3900 A., terminal blocks, must withstand short circuit test using the test currents and test durations specified Table 5.g.7) 3100 2 (33. After this, static heating test performed. . the tenth time, new conductor connected. After the test, the specimen must neither show evidence cracking, breaking melting, nor any changes electrical properties.2) 2450 3 (26.4) 1180 6 (13.com I Test specimen WAGO Rail-Mount Terminal Block Systems Technical Information • Conditioning Temperature-Rise Rest per 1059, 486 C • Grounding and Bonding Equipment per 467 Test performed per: UL 1059 (Rail-mount terminal blocks) 486 (Splicing wire connectors) Conditioning: The clamping units are pre-wired/pre-inserted nine times using conductor with maximum rated cross section.0) 8030 4/0 (107) 10100 250 kcmil (127) 12000 When used grounding and bonding equipment, e.3) 1530 4 (21