Page 108 Detailed description REG-DP/ REG-DPA parameters We take care it. a) Tuning+Correction Readjust set value At the end the transient earth fault time, the P-coil is readjusted set value. The coil adjusted to the resonance point and the current correction. The states the binary inputs must allocat- ed the switch information the feeders. The value for the corresponding binary input could be, for example, Ear_Corr1 for the feeder for dIc_1. this case, the P-coil is adjusted the last calculated resonance point. If lines are not switched off detect faults, 'Ires' can selected. If, the other hand, switch-offs switches other grids are performed isolate the earth fault, the current coil position must corrected the absolute value the switch- off switch. b) Ires+Correction Combination Ires and correction. Parameters Description Examples in Figure 77: None The coil position not readjusted when earth fault occurs. The values dIc_1 dIc_4 enable the coil posi- tion corrected for lines when earth fault occurs. At the end the transient earth fault time, the P-coil is adjusted the last calculated resonance point. Correction table when the CORR_TAB feature is selected. c) The correction table displayed when the CORR_TAB feature selected the 'General' menu. The determination the correction value described further down. . Ires Readjust the resonance point