0mm PVC/copper C Thermostat fed 2.5mm PVC/copper B switch fuse fed 4. Applying the diversity factor Table 1A Total current rating A First amperes A of 52 17 10 30 1 .753).20 Floor warming installations. . A A 30A Cables embedded in concrete floor 20A A Thermostat incorporating switch fed 2.5mm PVC/copper Lounge Hall Bedroom B B C C FIGURE 14. % 7 7 65 5 10 65 A A Socket outlet A Assessed current demand .Electrical installations and wiring systems 297 metallic grid connected the protective conductor the supply circuit (Regulation 701. Cooker circuit A cooker with rating above 3kW must supplied its own circuit but since unlikely that normal use every heating element will switched on the same time, diversity factor may applied calculating the cable size, detailed the Site Guide. . 65 . Consider, example, cooker with the following elements fed from a cooker control unit incorporating 13A socket: 4 8000 1 2000 1 kW fast boiling rings W kW grill W kW o oven W Total loading 000 W 2000 12 When connected 230 V Current rating 12000 230 52 17