ABB Softstartéry - komunikace (EN)

| Kategorie: Leták / Datasheet  | Tento dokument chci!

Vydal: ABB s.r.o, ELSYNN Autor: ABB ELSYnn

Strana 141 z 225







Poznámky redaktora
Binary input telegram To PLC from Softstarter. Word input data area Binary input byte Bit Data Description 0 relay output Status K4 1 relay output Status K5 2 relay output Status K6 3 Programmable software output Status V7 4 Start Input Status Start Input 5 Stop Input Status Stop Input 6 In0 Input Status In0 7 In1 Input Status In1 1 (0) Run Run Status 9 (1) Top Ramp Top Ramp Status 10 (2) Line Inside Delta connection Line, Delta 11 (3) Phase sequence L1,L2,L3 1=L1,L3,L2 12 (4) Prot Motor Event Status 13 (5) Prot Locked Rot Event Status 14 (6) Prot Underload Event Status 15 (7) Prot Phase Imb Event Status 1 Prot High Event Status 1 Prot Phase Rev Event Status 2 Prot PTC Event Status 3 Dummy 4 Prot SCR Event Status 5 Warn Event Status 6 Warn SCR Event Status 7 Warn I=High Event Status 3 (0) Warn I=Low Event Status 9 (1) Fault (general signal) Event Status, general for all faults 10 (2) Fault Phase Loss Event Status 11 (3) Fault SCR Event Status 12 (4) Fault Open SCR Event Status 13 (5) Fault Wrong Freq Event Status 14 (6) Fault Connection Event Status 15 (7) Fault Internal Event Status 2 Fault Timeout Event Status 1 Fault Temp Event Status 2 Fault Line side Event Status 3 Fault closed Event Status 4 Fault open Event Status 5 Dummy 6 Shunt Fault Event Status 7 Fault Line/Delta Event Status 5 (0) Local Control Other control, Key-pad control 9 (1) start start will probably cause a fault, start will probably not cause fault 10 (2) Spare (Value 0) 11 (3) Spare (Value 0) 12 (4) Spare (Value 0) 13 (5) Spare (Value 0) 14 (6) Spare (Value 0) 15 (7) Spare (Value 0) 1SFC132047M0201