50 mm² 300 300m 500 m System limit 250 addresses per LITECOM CCD 2,500 addresses with controllers the first LITECOM infinity generation, 100,000 addresses the final expansion stage.5 mm Type installation DIN rail mounting (35mm DIN rail acc.5 1. 50022) Space for only units required .00 mm² 200 200m 420 m 1. 3 DALI incl. cable length DALI Max. cable length LM Jointly with mains Jointly with mains in the same cable the same cable 0. DALI voltage supply with 120 bus loads (240mA) per DALI line 64 DALI units per DALI line 64 DALI units per DALI line 1 system bus (without bus power supply) Test switch and status LED for each DALI chain 1 Ethernet 100Mbits/s; RJ45/CAT Connection Plug-in screw terminals for one-wire fine-wire cables with cross-section ranging from 0.50 mm² 100 100 250 m 0. first generation LITECOM infinity system can comprise 2,500 addresses with to 15 controllers and ultimately to 100,000 addresses will possible. The system can thus flexibly adjusted if the requirements the building change.127 The Lighting Handbook LITECOM infinity: General information Technical data Application The number possible addresses adds by linking several LITECOM controllers. Permissible cable lengths Cable cross-section Max.75 mm² 150 150 350 m 1